Connection options for IEC-fans
WARNING:
Fans with Inverter: Terminals and connections have voltage even in a unit that is shut off. Electric shock. Wait for 15 minutes after disconnecting the voltage at all poles before opening the device. |
|
WARNING:
Ensure free space in front of the electrical cabinet according to local regulations. |
Electrical options for IEC-fans | Code | |
---|---|---|
Control panel | Motor Protective Switch Panel (always EMC) | B |
Starter Panel | SP | |
Motor Protective Switch Panel and Frequency Converter (always EMC) | BFC | |
Motor Protective Switch Panel, Frequency Converter and Temperature-probe (always EMC) | BFCT | |
Connection Box | Connection Box (Terminal Box) | CB |
Connection Box - EMC | CB…EMC |
Fan size ø 900 mm |
Fan size ø 1200 mm |
||||
---|---|---|---|---|---|
SRM™ |
Cable [m] |
SRD™ | Cable [m] | SRD™ | Cable [m] |
1A | 4.1 | 2A | 21.2 | 2A | 11.2 |
1B | 4.3 | 2B | 22.8 | 2B | 11.4 |
2A | 9.6 | 2C | 24.0 | 2C | 12.0 |
2B | 10.4 | 3A | 36.0 | 3A | 18.9 |
3A | 16.5 | 3B | 39.6 | 3B | 19.8 |
3B | 18.3 | 3C | 42.3 | 3C | 21.2 |
4A | 25.0 | 4A | 55.2 | 4A | 28.8 |
4B | 28.2 | 4B | 61.6 | 4B | 30.8 |
5A | 34.8 | 4C | 66.4 | 4C | 33.2 |
5B | 39.8 | 5A | 76.0 | 5A | 39.5 |
- | - | 5B | 86.0 | 5B | 43.0 |
- | - | 5C | 93.5 | 5C | 46.8 |
- | - | 6A | 99.6 | 6A | 51.6 |
- | - | 6B | 114 | 6B | 57.0 |
- | - | 6C | 125 | 6C | 62.4 |
- | - | 7A | 126 | 7A | 65.1 |
- | - | 7B | 130 | 7B | 64.7 |
- CB
- Connection box: Fan power supply cables are wired to the unit end. EMC is optional.
- SP
- Starter panel: The panel includes one main contactor. When you close the customer’s external potential free contact, all the fans go ON at the same time. When you open the contact, the fans go OFF. Fan power supply cables are wired to the unit end. The fan motors are supplied via tripping circuit breakers measuring both overcurrent and short circuit current. The electrical panel is equipped with a power main switch.
- B
- Motor protective switch panel: Fan power supply cables are wired to the unit end. The fan motors are supplied via tripping circuit breakers measuring both overcurrent and short circuit current. Customer only needs to bring main power to the electrical panel. The electrical panel is equipped with a power main switch. EMC is a standard option.
- BFC
- Motor protective switch panel and frequency converter: Inverter control provides continuous fan speed control for the liquid coolers. Fan power supply cables are wired to the unit end. The fan motors are supplied via tripping circuit breakers measuring both overcurrent and short circuit current. The electrical panel is equipped with a power main switch and a manual bypass switch. EMC is a standard option.
- BFCT
- Motor protective switch panel, frequency converter and temperature probe: Provides temperature control for the liquid coolers. Fan power supply cables are wired to the unit end. The fan motors are supplied via tripping circuit breakers measuring both overcurrent and short circuit current. The electrical panel is equipped with a power main switch and a manual bypass switch. EMC is a standard option.
Control panels have been pre-configured and test run at the factory, including a test run of the fans and inspection of the regulator. See the product-specific documentation of Alfa LU-VE Control Panels.
The delivery includes the necessary documentation for the control system and electrical panel. The documentation is in the electrical panel.
The cables corresponding to the EMC standard are connected to the unit end. See the normative cable lengths in Cable lengths for SR™ models. The lengths may be different when you are using special equipment or special cables. If the model type is not listed below, contact Fincoil LU-VE Oy for information.